Read Write IO in Excel using TwinCAT ADS-Script-DLL
You can control the IO in your program from Excel and develop a simple interface using Visual Basic thanks to the TwinCAT ADS - Script DLL.
If the developer options is not enabled in Excel, you need to enable this option first. Go to File-Options in Excel and select the 'Customize Ribbon' option on the following menu and check the Developer under Main Tabs options.
Since we will create a macro and save our script, click the 'Save' option and change the file format to 'Excel-Macro-Enabled Workbook'.
Create a macro in Excel.
Select the 'Visual Basic' under Developer menu and right click on somewhere on the project explorer, select 'Insert' , then 'Userform'.
Now you can create your own interface using input box, label, buttons etc.. from the toolbox. For this tutorial we simply created a pump control application. This simple interface allows you to connect to IPC, read/write the ADS State, set/read the water flow value and turn on/off the pump.
Add the variables below in your global variable list called 'GVL_IO' .
//for pump control IgbPumpControl AT %MX20.0 : BOOL := FALSE; //true- pump on, false - pump off OgbPumpStatus AT %MX20.1 : BOOL := FALSE; IgfWaterFlow AT %MB18 : REAL := 0; OgfWaterFlow AT %MB18 : REAL := 0;
Add the code below in your MAIN program.
OgbPumpStatus := IgbPumpControl; OgfWaterFlow := IgfWaterFlow;
Build the solution, activate the configuration and login the PLC. Now we will add the visual basic script in Excel to read/write the variables. Using TwinCAT ADS-Script-DLL, you can either use the Index-Group and Index-Offset of a variable or the name of the variable to control it.
To see the Index-Group and Index-Offset of a variable, you can use the 'Target Browser'.
When you are logged in the PLC, on the menu select 'Target Browser', and choose port '851' (PLC Port), and expand the GVL_IO. You can see all the Index-Group and Index-Offset of the variables in this global variable list.
Now we need to add the ADS-Script library in Excel. In the Visual Basic editor window, select the 'Tools', then 'References'.
Select the checkbox of 'Beckhoff TcScript' dll and click OK.
Right click your form and select 'View Code'.
Add the public declarations in the form's script editor.
Public TcClientSync As TCSCRIPTLib.TcScriptSync Public nAdsAmsPortNum As Integer Public strAdsAmsNetId As String
strAdsAmsNetId is the AMS Net ID of the IPC. For Local Target, you could either use "" or "0.0.0.0.0.0".
nAdsAmsPortNum is the ADS Port Number. You can check this tutorial if you want to enable the ADS Server for your EtherCAT Master and use that port number in Excel.
Connecting to IPC:
The lines below enables you to connect to IPC.
Set TcClientSync = CreateObject("TcScript.TcScriptSync")
Call TcClientSync.ConnectTo(strAdsAmsNetId, nAdsAmsPortNum)
Read a Boolean variable using the Index-Group and Index-Offset:
You can create a function and use this function in the main part of your program. To read a boolean variable with this method, we will need to pass TcClientSync object, index group and the index offset to our function.
Private Function ReadBoolVar(TcClientSync As TCSCRIPTLib.TcScriptSync, indexGroup As Long, indexOffset As Long) As Boolean
On Error GoTo errFunc
ReadBoolVar = TcClientSync.ReadBool(indexGroup, indexOffset)
Exit Function
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Function
You can use call this function as shown below:
'read bool by index group and offset Dim result As Boolean result = ReadBoolVar(TcClientSync, &H4021&, &H418&) MsgBox (result)
&H4021& - Index Group, &H418& - Index Offset. How to getting these values is explained above already.
Read a Boolean variable using its path:
Reading the value of a variable by name is a way easier method. All you need is to the path of the variable name.
Private Function ReadBoolByName(TcClientSync As TCSCRIPTLib.TcScriptSync, VarName As String) As Boolean
On Error GoTo errFunc
ReadBoolByName = TcClientSync.ReadVar(VarName)
Exit Function
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Function
Dim bPumpState As Boolean bPumpState = ReadBoolByName(TcClientSync, "GVL_IO.OgbPumpStatus")
Write a Boolean variable using the Index-Group and Index-Offset:
Private Function WriteBoolVar(TcClientSync As TCSCRIPTLib.TcScriptSync, indexGroup As Long, indexOffset As Long, varBool As Boolean)
On Error GoTo errFunc
Call TcClientSync.WriteBool(indexGroup, indexOffset, varBool)
Exit Function
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Function
'write bool Dim bWriteVar As Boolean bWriteVar = True Call WriteBoolVar(TcClientSync, &H4021&, &H419&, bWriteVar)
Write a Boolean variable using its path:
Private Function WriteBoolByName(TcClientSync As TCSCRIPTLib.TcScriptSync, VarName As String, varBool As Boolean)
On Error GoTo errFunc
Call TcClientSync.WriteVar(VarName, varBool)
Exit Function
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Function
'write bool by name Call WriteBoolByName(TcClientSync, "GVL_IO.IgbProxSensor", False)
Read/Write ADS State
You can also Stop and Run your plc application using the ADS State. You can write '5' to run the PLC and 6 to stop.
Read the ADS State:
AdsState.Caption = TcClientSync.ReadAdsState()
Write the ADS State:
If (ADSStateWriteBox.Text <> TcClientSync.ReadAdsState()) Then
Call TcClientSync.WriteAdsState(ADSStateWriteBox.Text) '5 for run, 6 for stop
End If
You can also use the same methods to read/write integer, real, string etc.. Here's the full visual script code for this simple interface. You can also see the implementation read/write for other data types in this code.
Public TcClientSync As TCSCRIPTLib.TcScriptSync
Public nAdsAmsPortNum As Integer
Public strAdsAmsNetId As String
Private Sub Connect_Click()
On Error GoTo errFunc
nAdsAmsPortNum = CLng(PortNumber.Text)
If (Len(AmsNetIDInputBox.Text) > 0) Then
strAdsAmsNetId = AmsNetIDInputBox.Text
Else
strAdsAmsNetId = ""
End If
Set TcClientSync = CreateObject("TcScript.TcScriptSync")
Call TcClientSync.ConnectTo(strAdsAmsNetId, nAdsAmsPortNum)
Exit Sub
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Sub
Private Sub PumpControl_Click()
On Error GoTo errFunc
Dim bPumpState As Boolean
If PumpControl.Value = False Then
PumpControl.Caption = "Turn On Pump"
Call WriteBoolByName(TcClientSync, "GVL_IO.IgbPumpControl", False)
Else
PumpControl.Caption = "Turn Off Pump"
Call WriteBoolByName(TcClientSync, "GVL_IO.IgbPumpControl", True)
End If
Application.Wait (Now + TimeValue("0:00:01")) '1s delay
bPumpState = ReadBoolByName(TcClientSync, "GVL_IO.OgbPumpStatus")
If bPumpState = True Then
PumpState.Caption = "Pump is On"
Else
PumpState.Caption = "Pump is Off"
End If
Exit Sub
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Sub
Private Sub ReadFlow_Click()
On Error GoTo errFunc
Dim fFlow As Single
Dim sPLCPathFlow As String
sPLCPathFlow = "GVL_IO.OgfWaterFlow"
fFlow = ReadRealByName(TcClientSync, sPLCPathFlow)
ReadFlowInputBox.Caption = CStr(fFlow) + " " + "gpm"
Exit Sub
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Sub
Private Sub ReadState_Click()
On Error GoTo errFunc
AdsState.Caption = TcClientSync.ReadAdsState()
Exit Sub
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Sub
Private Sub WriteAdsState_Click()
On Error GoTo errFunc
If (ADSStateWriteBox.Text <> "") Then
If (ADSStateWriteBox.Text <> TcClientSync.ReadAdsState()) Then
Call TcClientSync.WriteAdsState(ADSStateWriteBox.Text)
End If
End If
Exit Sub
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Sub
Private Sub SetFlow_Click()
On Error GoTo errFunc
Dim fFlow As Single
Dim sPLCPathFlow As String
sPLCPathFlow = "GVL_IO.IgfWaterFlow"
If (SetFlowInputBox.Text <> "") Then
fFlow = CSng(SetFlowInputBox.Text)
Call WriteRealByName(TcClientSync, sPLCPathFlow, fFlow)
SetFlowInputBox.Text = fFlow
End If
Exit Sub
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Sub
Private Function WriteBoolVar(TcClientSync As TCSCRIPTLib.TcScriptSync, indexGroup As Long, indexOffset As Long, varBool As Boolean)
On Error GoTo errFunc
Call TcClientSync.WriteBool(indexGroup, indexOffset, varBool)
Exit Function
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Function
Private Function WriteBoolByName(TcClientSync As TCSCRIPTLib.TcScriptSync, VarName As String, varBool As Boolean)
On Error GoTo errFunc
Call TcClientSync.WriteVar(VarName, varBool)
Exit Function
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Function
Private Function WriteRealByName(TcClientSync As TCSCRIPTLib.TcScriptSync, VarName As String, varReal As Single)
On Error GoTo errFunc
Call TcClientSync.WriteVar(VarName, varReal)
Exit Function
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Function
Private Function WriteIntByName(TcClientSync As TCSCRIPTLib.TcScriptSync, VarName As String, varInt As Integer)
On Error GoTo errFunc
Call TcClientSync.WriteVar(VarName, varInt)
Exit Function
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Function
Private Function ReadBoolVar(TcClientSync As TCSCRIPTLib.TcScriptSync, indexGroup As Long, indexOffset As Long) As Boolean
On Error GoTo errFunc
ReadBoolVar = TcClientSync.ReadBool(indexGroup, indexOffset)
Exit Function
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Function
Private Function ReadBoolByName(TcClientSync As TCSCRIPTLib.TcScriptSync, VarName As String) As Boolean
On Error GoTo errFunc
ReadBoolByName = TcClientSync.ReadVar(VarName)
Exit Function
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Function
Private Function ReadRealByName(TcClientSync As TCSCRIPTLib.TcScriptSync, VarName As String) As Single
On Error GoTo errFunc
ReadRealByName = TcClientSync.ReadVar(VarName)
Exit Function
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Function
Private Function ReadIntByName(TcClientSync As TCSCRIPTLib.TcScriptSync, VarName As String) As Integer
On Error GoTo errFunc
ReadIntByName = TcClientSync.ReadVar(VarName)
Exit Function
errFunc:
MsgBox "Error: (0x" & Format(Hex(Err.Number), "00000000") & "), " & Err.Description
End Function
You can find more information on TwinCAT ADS-Script-DLL here.