I am writing to inquire about an unusual issue we have encountered while controlling a servo motor using the TwinCAT system.

Currently, we are operating the motor by inputting the target position and velocity into the MoveAbsolute function block. While monitoring the servo motor's actual position (GVL.Axis1.NcToPlc.ModuloActPos) using the Scope function, we noticed a strange behavior: during the initial phase of the movement, the actual position lags behind the target position. However, after a certain point, the actual position starts to lead the target position by approximately 1 degree.

Unlike a standard following error (lagging), it is difficult for us to pinpoint why the motor would move ahead of the target position. Therefore, we are reaching out for your assistance.

To help with your investigation, I have attached the relevant test files. In the attached test_profile.csv file, 'F' represents the velocity and 'U' represents the target position.

We would greatly appreciate your insights into the potential causes of this issue and any recommendations on additional parameters or settings we should inspect.

Additionally, I have provided the PLC code below.

Thank you for your support.

PROGRAM MAIN
VAR
Robot1: FB_FANUC_Basic;
bReset: BOOL;
RobotEnable, RobotFault: BOOL;
 
// Buffer
send_single_buffer_v2 : ARRAY[0..6] OF REAL;
goto_buffer : ARRAY[0..6] OF REAL; // Buffer to move robot for manual
 
send_buffer1_1_v2, send_buffer1_2_v2, send_buffer1_3_v2,
send_buffer2_1_v2, send_buffer2_2_v2, send_buffer2_3_v2: ARRAY[0..146] OF REAL;
 
// Function Block
fb_custom_service : FB_CUSTOM_SERVICE; // Send a Sequence Data to Robot
 
fbMove1, fbMove2, fbHome : MC_MoveModulo; // Turn Table Motor Move, Only Turn Table Motor Move, Turn Table Motor Homing
fbMove : MC_MoveAbsolute;
fbMove_rev1, fbMove_rev2, fbMove_rot1, fbMove_rot2 : MC_MoveVelocity; // Revolution & Rotation Motor Move
 
fbReset : MC_Reset; // Motor Reset
 
fbPower, fbPower_rev, fbPower_rot : MC_Power; // Motor Power On
 
mc_readactpos : MC_ReadActualPosition; // Read Position of Turn Table Motor
mc_readactvel_rev, mc_readactvel_rot : MC_ReadActualVelocity; // Read Velocity of Revolution & Rotation Motor
 
mc_stop, mc_stop_rev, mc_stop_rot : MC_Stop; // Motor Stop
mc_setpos: MC_SetPosition;
bSetDone: BOOL;
 
fbTimer_SetPos: TON;
bTimer: BOOL;
REdge_setdone: R_TRIG;
 
 
// Variables
// Bool
bExecute : BOOL; // fb_custom_service.Execute
motor_trig1, motor_trig2 : BOOL; // Signal for cross-action of Motors
bStopDone, bStopDone_rev, bStopDone_rot : BOOL; // Stopped Rising Edge Signal
bHomeDone : BOOL; // Hoiming Done Signal
// LREAL
nPos, nVel : LREAL; // Input Data of Turn Table Motor
fServoCurrPos, fServoCurrVel_rev, fServoCurrVel_rot : LREAL; // Output Data of the Motors
// INT
nState : INT:= 0;
nPointIdx : INT:= 1;
 
trig_status : INT:= 0;
// fb_custom_service variables
nServiceCode : BYTE;
nClass, nInstance, nAttribute : WORD;
 
nNumberofData : DINT;
nBufferID : INT;
pCurrentAddr : PVOID;
nCurrentSize : WORD;
 
nErrId : UDINT;
error : STRING;
 
// Rising Edge Trigger
REdge_first : R_TRIG;
REdge_StopDone : R_TRIG;
REdge_StopDone_rev : R_TRIG;
REdge_StopDone_rot : R_TRIG;
REdge_Restart : R_TRIG;
REdge_HomeDone : R_TRIG;
REdge_DO48 : R_TRIG;
 
bWaitCheckPoint: BOOL;
nNextState: INT;
bRobotAck: BOOL;
 
bInit : BOOL:= TRUE;
bFirstStart : BOOL:= TRUE;
bNextStepReq : BOOL;
nCntIdx : INT;
 
fbScanTimer : TON;
fbSetOverride : MC_SetOverride;
 
fRobotFirstPos: LREAL;
fRobotStartPos, fRobotTargetPos, fRobotActualPos,
fRobotTotalDist, fRobotRemainRatio,
fMotorStartPos, fMotorTargetPos, fMotorActualPos,
fMotorTotalDist, fMotorVirtualTarget : LREAL;
 
fSampledTargetPos, fSampledActualPos : LREAL;
 
fOutput : LREAL;
fCalculatedOverride : LREAL:= 0.0;
 
nPos_X: UDINT:= 0;
nPos_Y: UDINT:= 0;
fBackupValue: LREAL;
fRelativePos: LREAL;
REdge_bStart: R_TRIG;
 
fScaled_Kp: LREAL;
fDrivePosLoopGain: LREAL:= 32.0;
fPositionError: LREAL;
 
bSequenceMode: BOOL:= FALSE;
nXorY: INT;
nRobotIdx: UDINT:=0;
nRobotIdx_int: INT;
frobot: LREAL;
nTrackingIdx: INT:= 1;
nTotalProcessCnt: DINT:= 1;
END_VAR
 
Robot1.Update();
RobotEnable:= Robot1.qEnable;
RobotFault:= Robot1.qFault;
 
CASE nBufferID OF
1:
pCurrentAddr:= ADR(send_single_buffer_v2);
nCurrentSize:= SIZEOF(send_single_buffer_v2);
2:
pCurrentAddr:= ADR(goto_buffer);
nCurrentSize:= SIZEOF(goto_buffer);
11:
pCurrentAddr:= ADR(send_buffer1_1_v2);
nCurrentSize:= SIZEOF(send_buffer1_1_v2);
12:
pCurrentAddr:= ADR(send_buffer1_2_v2);
nCurrentSize:= SIZEOF(send_buffer1_2_v2);
13:
pCurrentAddr:= ADR(send_buffer1_3_v2);
nCurrentSize:= SIZEOF(send_buffer1_3_v2);
21:
pCurrentAddr:= ADR(send_buffer2_1_v2);
nCurrentSize:= SIZEOF(send_buffer2_1_v2);
22:
pCurrentAddr:= ADR(send_buffer2_2_v2);
nCurrentSize:= SIZEOF(send_buffer2_2_v2);
23:
pCurrentAddr:= ADR(send_buffer2_3_v2);
nCurrentSize:= SIZEOF(send_buffer2_3_v2);
99:
pCurrentAddr:= ADR(nNumberofData);
nCurrentSize:= SIZEOF(nNumberofData);
END_CASE
 
 
fb_custom_service(
sNetId:= '192.168.0.196.3.1', 
sIPv4Addr:= '100.100.100.1', 
bExecute:= bExecute, 
nServiceCode:= nServiceCode, 
nClass:= nClass, 
nInstance:= nInstance, 
nAttribute:= nAttribute, 
pSrc:= pCurrentAddr, 
nSrcDataLen:= nCurrentSize, 
);
 
error:= F_GET_ETHERNETIP_ERROR_TEXT(nErrorId:= nErrId);
 
 
fbPower(Axis:= GVL.Axis1, Enable:= TRUE, Enable_Positive:= TRUE, Enable_Negative:= TRUE, Override:= 100.0);
fbPower_rev(Axis:= GVL.Axis2, Enable:= TRUE, Enable_Positive:= TRUE, Enable_Negative:= TRUE, Override:= 100.0);
fbPower_rot(Axis:= GVL.Axis3, Enable:= TRUE, Enable_Positive:= TRUE, Enable_Negative:= TRUE, Override:= 100.0);
fbReset(Axis:= GVL.Axis1, Execute:= GVL.bReset);
 
IF GVL.bReset THEN
nState:= 0;
GVL.bStart:= FALSE;
GVL.bReqUpdateLower:= FALSE;
GVL.bReqUpdateUpper:= FALSE;
END_IF
 
CASE nState OF
0:
IF GVL.bStart THEN
nPointIdx:= 1;
nState:= 10;
END_IF
10:
fbMove1.Position:= GVL.aPathData[nPointIdx].fPosition;
fbMove1.Velocity:= GVL.aPathData[nPointIdx].fVelocity;
fbMove1.BufferMode:= MC_BufferMode.MC_Aborting;
fbMove1.Direction:= MC_Positive_Direction;
fbMove1.Execute:= TRUE;
 
fbMove_rev1.Velocity:= GVL.aPathData[nPointIdx].fVelocity2;
fbMove_rev1.BufferMode:= MC_BufferMode.MC_Aborting;
fbMove_rev1.Execute:= TRUE;
 
fbMove_rot1.Velocity:= GVL.aPathData[nPointIdx].fVelocity3;
fbMove_rot1.BufferMode:= MC_BufferMode.MC_Aborting;
fbMove_rot1.Execute:= TRUE;
 
IF fbMove1.Active AND fbMove_rev1.Active AND fbMove_rot1.Active THEN
fbMove1.Execute:= FALSE;
fbMove_rev1.Execute:= FALSE;
fbMove_rot1.Execute:= FALSE;
nPointIdx:= nPointIdx + 1;
motor_trig1:= TRUE;
nState:= 20;
END_IF
 
20:
fbMove2.Position:= GVL.aPathData[nPointIdx].fPosition;
fbMove2.Velocity:= GVL.aPathData[nPointIdx].fVelocity;
fbMove2.BufferMode:= MC_BufferMode.MC_BlendingPrevious;
fbMove2.Direction:= MC_Positive_Direction;
 
fbMove_rev2.Velocity:= GVL.aPathData[nPointIdx].fVelocity2;
fbMove_rev2.BufferMode:= MC_BufferMode.MC_BlendingPrevious;
 
fbMove_rot2.Velocity:= GVL.aPathData[nPointIdx].fVelocity3;
fbMove_rot2.BufferMode:= MC_BufferMode.MC_BlendingPrevious;
 
IF motor_trig1 THEN
IF GVL.aPathData[nPointIdx].fVelocity > 0.0 THEN
fbMove2.Execute:= TRUE;
fbMove_rev2.Execute:= TRUE;
fbMove_rot2.Execute:= TRUE;
ELSE
motor_trig1:= FALSE;
nState:= 99;
END_IF
END_IF
IF fbMove2.Active AND fbMove_rev2.Active AND fbMove_rot2.Active THEN
fbMove2.Execute:= FALSE;
fbMove_rev2.Execute:= FALSE;
fbMove_rot2.Execute:= FALSE;
motor_trig1:= FALSE;
nPointIdx:= nPointIdx + 1;
nTotalProcessCnt:= nTotalProcessCnt + 1;
 
IF (nTotalProcessCnt > 1) AND (((nTotalProcessCnt - 1) MOD 63) = 0) THEN
bWaitCheckPoint:= TRUE;
END_IF
IF nPointIdx = 501 THEN
GVL.bReqUpdateLower:= TRUE;
ELSIF nPointIdx > GVL.nMaxPoints THEN
nPointIdx:= 1;
IF NOT GVL.bAllDataFinished THEN
GVL.bReqUpdateUpper:= TRUE;
END_IF
END_IF
IF nState <> 99 THEN
IF bWaitCheckPoint THEN
nNextState:= 30;
nState:= 40;
ELSE
motor_trig2:= TRUE;
nState:= 30;
END_IF
END_IF
ELSIF fbMove2.Error THEN
nState:= 900;
END_IF
30:
fbMove1.Position:= GVL.aPathData[nPointIdx].fPosition;
fbMove1.Velocity:= GVL.aPathData[nPointIdx].fVelocity;
fbMove1.BufferMode:= MC_BufferMode.MC_BlendingPrevious;
fbMove1.Direction:= MC_Positive_Direction;
 
fbMove_rev1.Velocity:= GVL.aPathData[nPointIdx].fVelocity2;
fbMove_rev1.BufferMode:= MC_BufferMode.MC_BlendingPrevious;
 
fbMove_rot1.Velocity:= GVL.aPathData[nPointIdx].fVelocity3;
fbMove_rot1.BufferMode:= MC_BufferMode.MC_BlendingPrevious;
 
IF motor_trig2 THEN
IF GVL.aPathData[nPointIdx].fVelocity > 0.0 THEN
fbMove1.Execute:= TRUE;
fbMove_rev1.Execute:= TRUE;
fbMove_rot1.Execute:= TRUE;
ELSE
motor_trig2:= FALSE;
nState:= 99;
END_IF
END_IF
IF fbMove1.Active AND fbMove_rev1.Active AND fbMove_rot1.Active THEN
fbMove1.Execute:= FALSE;
fbMove_rev1.Execute:= FALSE;
fbMove_rot1.Execute:= FALSE;
motor_trig2:= FALSE;
nPointIdx:= nPointIdx + 1;
nTotalProcessCnt:= nTotalProcessCnt + 1;
 
IF (nTotalProcessCnt > 1) AND (((nTotalProcessCnt - 1) MOD 63) = 0) THEN
bWaitCheckPoint:= TRUE;
END_IF
IF nPointIdx = 501 THEN
GVL.bReqUpdateLower:= TRUE;
ELSIF nPointIdx > GVL.nMaxPoints THEN
nPointIdx:= 1;
IF NOT GVL.bAllDataFinished THEN
GVL.bReqUpdateUpper:= TRUE;
END_IF
END_IF
IF nState <> 99 THEN
IF bWaitCheckPoint THEN
nNextState:= 20;
nState:= 40;
ELSE
motor_trig1:= TRUE;
nState:= 20;
END_IF
END_IF
ELSIF fbMove1.Error THEN
nState:= 900;
END_IF
 
40:
IF Robot1._UO1.DO237 THEN
Robot1._UI1.DI44:= TRUE;
bRobotAck:= TRUE;
END_IF
 
IF bRobotAck AND NOT Robot1._UO1.DO237 THEN
Robot1._UI1.DI44:= FALSE;
bRobotAck:= FALSE;
bWaitCheckPoint:= FALSE;
 
IF nNextState = 20 THEN
motor_trig1 := TRUE;
ELSIF nNextState = 30 THEN
motor_trig2 := TRUE;
END_IF
nState := nNextState;
END_IF
 
99:
IF NOT fbMove1.Busy AND NOT fbMove2.Busy THEN
IF Robot1._UO1.DO237 THEN
Robot1._UI1.DI44:= TRUE;
ELSE
Robot1._UI1.DI44:= FALSE;
nState:= 0;
nPointIdx:= 1;
nTrackingIdx:= 1;
 
motor_trig1:= FALSE;
motor_trig2:= FALSE;
 
bWaitCheckPoint:= FALSE;
bRobotAck:= FALSE;
nNextState:= 0;
 
fbMove1.Execute:= FALSE;
fbMove2.Execute:= FALSE;
fbMove_rev1.Execute:= FALSE;
fbMove_rev2.Execute:= FALSE;
fbMove_rot1.Execute:= FALSE;
fbMove_rot2.Execute:= FALSE;
 
GVL.bStart:= FALSE;
IF NOT GVL.bStop_rev THEN
GVL.bStop_rev:= TRUE;
END_IF
IF NOT GVL.bStop_rot THEN
GVL.bStop_rot:= TRUE;
END_IF
bSequenceMode:= FALSE;
END_IF
END_IF
900:
IF NOT fbMove1.Busy AND NOT fbMove2.Busy THEN
GVL.bStart:= FALSE;
nState:= 0;
nPointIdx:= 1;
nCntIdx:= 0;
bSequenceMode:= FALSE;
END_IF
 
END_CASE
 
fbMove1(Axis:= GVL.Axis1);
fbMove2(Axis:= GVL.Axis1);
fbMove_rev1(Axis:= GVL.Axis2);
fbMove_rev2(Axis:= GVL.Axis2);
fbMove_rot1(Axis:= GVL.Axis3);
fbMove_rot2(Axis:= GVL.Axis3);
 
IF GVL.bReqUpdateLower AND GVL.bUpdateDone THEN
GVL.bReqUpdateLower:= FALSE;
END_IF
IF GVL.bReqUpdateUpper AND GVL.bUpdateDone THEN
GVL.bReqUpdateUpper:= FALSE;
END_IF
 
REdge_first(CLK:= MAIN.Robot1._UO1.DO45);
IF REdge_first.Q THEN
GVL.bStart:= TRUE;
END_IF
 
fbMove(
Axis:= GVL.Axis1,
Execute:= GVL.bStart2,
Position:= nPos,
Velocity:= nVel
);
 
fbHome(
Axis:= GVL.Axis1, 
Execute:= GVL.bHome, 
Position:= 0.0, 
Velocity:= 10, 
Direction:= MC_Direction.MC_Shortest_Way, 
Done=> bHomeDone, 
);
 
mc_readactpos(
Axis:= GVL.Axis1, 
Enable:= TRUE,  
Position=> fServoCurrPos
);
 
mc_readactvel_rev(
Axis:= GVL.Axis2, 
Enable:= TRUE, 
ActualVelocity=> fServoCurrVel_rev
);
 
mc_readactvel_rot(
Axis:= GVL.Axis3, 
Enable:= TRUE, 
ActualVelocity=> fServoCurrVel_rot
);
 
mc_stop(
Axis:= GVL.Axis1, 
Execute:= GVL.bStop, 
Done=> bStopDone, 
);
 
mc_stop_rev(
Axis:= GVL.Axis2, 
Execute:= GVL.bStop_rev,  
Done=> bStopDone_rev, 
);
 
mc_stop_rot(
Axis:= GVL.Axis3, 
Execute:= GVL.bStop_rot, 
Done=> bStopDone_rot, 
);
 
mc_setpos(
Axis:= GVL.Axis1,
Position:= 0.0,
Done=> bSetDone
);
 
REdge_HomeDone(CLK:= bHomeDone);
IF REdge_HomeDone.Q THEN
GVL.bHome:= FALSE;
bTimer:= TRUE;
END_IF
fbTimer_SetPos(IN:= bTimer, PT:= T#1S);
IF fbTimer_SetPos.Q THEN
mc_setpos.Execute:= TRUE;
END_IF
REdge_setdone(CLK:= bSetDone);
IF REdge_setdone.Q THEN
mc_setpos.Execute:= FALSE;
bTimer:= FALSE;
END_IF
 
REdge_StopDone(CLK:= bStopDone);
IF REdge_StopDone.Q THEN
GVL.bStart := FALSE;
GVL.bStart2 := FALSE;
IF motor_trig1 THEN
trig_status:= 1;
motor_trig1:= FALSE;
fbMove2.Execute:= FALSE;
fbMove_rev2.Execute:= FALSE;
fbMove_rot2.Execute:= FALSE;
ELSIF motor_trig2 THEN
trig_status:= 2;
motor_trig2:= FALSE;
fbMove1.Execute:= FALSE;
fbMove_rev1.Execute:= FALSE;
fbMove_rot1.Execute:= FALSE;
END_IF
GVL.bStop:= FALSE;
END_IF
 
REdge_StopDone_rev(CLK:= bStopDone_rev);
IF REdge_StopDone_rev.Q THEN
GVL.bStop_rev:= FALSE;
END_IF
 
REdge_StopDone_rot(CLK:= bStopDone_rot);
IF REdge_StopDone_rot.Q THEN
GVL.bStop_rot:= FALSE;
END_IF
 
REdge_Restart(CLK:= GVL.bRestart);
IF REdge_Restart.Q THEN
GVL.bStart:= TRUE;
IF trig_status = 1 THEN
motor_trig1:= TRUE;
ELSIF trig_status = 2 THEN
motor_trig2:= TRUE;
END_IF
GVL.bRestart:= FALSE;
END_IF
 
nPos_X.0:= Robot1._UO1.Xl0;
nPos_X.1:= Robot1._UO1.Xl1;
nPos_X.2:= Robot1._UO1.Xl2;
nPos_X.3:= Robot1._UO1.Xl3;
nPos_X.4:= Robot1._UO1.Xl4;
nPos_X.5:= Robot1._UO1.Xl5;
nPos_X.6:= Robot1._UO1.Xl6;
nPos_X.7:= Robot1._UO1.Xl7;
nPos_X.8:= Robot1._UO1.Xl8;
nPos_X.9:= Robot1._UO1.Xl9;
nPos_X.10:= Robot1._UO1.Xl10;
nPos_X.11:= Robot1._UO1.Xl11;
nPos_X.12:= Robot1._UO1.Xl12;
nPos_X.13:= Robot1._UO1.Xl13;
nPos_X.14:= Robot1._UO1.Xl14;
nPos_X.15:= Robot1._UO1.Xl15;
nPos_X.16:= Robot1._UO1.Xh0;
nPos_X.17:= Robot1._UO1.Xh1;
nPos_X.18:= Robot1._UO1.Xh2;
nPos_X.19:= Robot1._UO1.Xh3;
nPos_X.20:= Robot1._UO1.Xh4;
nPos_X.21:= Robot1._UO1.Xh5;
nPos_X.22:= Robot1._UO1.Xh6;
nPos_X.23:= Robot1._UO1.Xh7;
 
nPos_Y.0:= Robot1._UO1.Yl0;
nPos_Y.1:= Robot1._UO1.Yl1;
nPos_Y.2:= Robot1._UO1.Yl2;
nPos_Y.3:= Robot1._UO1.Yl3;
nPos_Y.4:= Robot1._UO1.Yl4;
nPos_Y.5:= Robot1._UO1.Yl5;
nPos_Y.6:= Robot1._UO1.Yl6;
nPos_Y.7:= Robot1._UO1.Yl7;
nPos_Y.8:= Robot1._UO1.Yl8;
nPos_Y.9:= Robot1._UO1.Yl9;
nPos_Y.10:= Robot1._UO1.Yl10;
nPos_Y.11:= Robot1._UO1.Yl11;
nPos_Y.12:= Robot1._UO1.Yl12;
nPos_Y.13:= Robot1._UO1.Yl13;
nPos_Y.14:= Robot1._UO1.Yl14;
nPos_Y.15:= Robot1._UO1.Yl15;
nPos_Y.16:= Robot1._UO1.Yh0;
nPos_Y.17:= Robot1._UO1.Yh1;
nPos_Y.18:= Robot1._UO1.Yh2;
nPos_Y.19:= Robot1._UO1.Yh3;
nPos_Y.20:= Robot1._UO1.Yh4;
nPos_Y.21:= Robot1._UO1.Yh5;
nPos_Y.22:= Robot1._UO1.Yh6;
nPos_Y.23:= Robot1._UO1.Yh7;
 
IF nXorY = 0 THEN
fRobotActualPos:= UDINT_TO_LREAL(nPos_X) / 1000.0;
IF Robot1._UO1.X_Check THEN
fRobotActualPos:= fRobotActualPos * (-1);
END_IF
ELSIF nXorY = 1 THEN
fRobotActualPos:= UDINT_TO_LREAL(nPos_Y) / 1000.0;
IF Robot1._UO1.Y_Check THEN
fRobotActualPos:= fRobotActualPos * (-1);
END_IF
END_IF
 
REdge_bStart(CLK:= Robot1._UI1.UI09_RSR1);
IF REdge_bStart.Q THEN
fBackupValue:= fRobotActualPos;
bSequenceMode:= TRUE;
 
(*fRobotTargetPos := fRobotFirstPos; 
fRobotStartPos  := fRobotFirstPos;
fMotorTargetPos := 0.0;
fMotorStartPos  := 0.0;*)
 
nTotalProcessCnt:= 1;
nTrackingIdx:= 1;
fRobotTargetPos:= GVL.aPathData[1].fRobot_Pos;
fRobotStartPos:= fRobotFirstPos;
fMotorTargetPos:= GVL.aPathData[1].fPosition;
fMotorStartPos:= 0.0;
 
fRobotTotalDist := 0.0;
fRobotRemainRatio := 0.0;
 
fSampledTargetPos := GVL.Axis1.NcToPlc.ModuloActPos; 
fPositionError := 0.0;
fOutput := 0.0;
 
fCalculatedOverride := 0.8;
END_IF
fRelativePos:= fRobotActualPos - fBackupValue;
 
IF bSequenceMode THEN
IF ABS(fRelativePos) >= ABS(fRobotTargetPos) THEN
nTrackingIdx:= nTrackingIdx + 1;
IF nTrackingIdx > GVL.nMaxPoints THEN
nTrackingIdx:= 1;
fRobotTargetPos:= GVL.aPathData[nTrackingIdx].fRobot_Pos;
fRobotStartPos:= GVL.aPathData[GVL.nMaxPoints].fRobot_Pos;
fMotorTargetPos:= GVL.aPathData[nTrackingIdx].fPosition;
fMotorStartPos:= GVL.aPathData[GVL.nMaxPoints].fPosition;
ELSE
fRobotTargetPos:= GVL.aPathData[nTrackingIdx].fRobot_Pos;
fRobotStartPos:= GVL.aPathData[nTrackingIdx - 1].fRobot_Pos;
fMotorTargetPos:= GVL.aPathData[nTrackingIdx].fPosition;
fMotorStartPos:= GVL.aPathData[nTrackingIdx - 1].fPosition;
END_IF
END_IF
END_IF
 
fbScanTimer(IN:= NOT fbScanTimer.Q, PT:= T#10MS);
IF fbScanTimer.Q THEN
fRobotTotalDist:= fRobotTargetPos - fRobotStartPos;
IF fRobotTotalDist <> 0 THEN
fRobotRemainRatio:= (fRobotTargetPos - fRelativePos) / fRobotTotalDist;
ELSE
fRobotRemainRatio:= 0.0;
END_IF
 
IF fMotorTargetPos = 0 THEN
fMotorTargetPos:= 360;
END_IF
fMotorTotalDist:= fMotorTargetPos - fMotorStartPos;
fMotorVirtualTarget:= fMotorTargetPos - (fMotorTotalDist * fRobotRemainRatio);
 
fSampledTargetPos:= fMotorVirtualTarget;
fSampledActualPos:= GVL.Axis1.NcToPlc.ModuloActPos;
END_IF
 
fScaled_Kp:= fDrivePosLoopGain / 500.0;
fPositionError:= fSampledTargetPos - fSampledActualPos;
 
fOutput:= fPositionError * fScaled_Kp;
 
fCalculatedOverride:= LIMIT(0.5, (0.8 + fOutput), 1.0);
 
nRobotIdx.0:= Robot1._UO1.DO221;
nRobotIdx.1:= Robot1._UO1.DO222;
nRobotIdx.2:= Robot1._UO1.DO223;
nRobotIdx.3:= Robot1._UO1.DO224;
nRobotIdx.4:= Robot1._UO1.DO225;
nRobotIdx.5:= Robot1._UO1.DO226;
nRobotIdx.6:= Robot1._UO1.DO227;
nRobotIdx.7:= Robot1._UO1.DO228;
nRobotIdx.8:= Robot1._UO1.DO229;
nRobotIdx.9:= Robot1._UO1.DO230;
nRobotIdx.10:= Robot1._UO1.DO231;
nRobotIdx.11:= Robot1._UO1.DO232;
nRobotIdx.12:= Robot1._UO1.DO233;
nRobotIdx.13:= Robot1._UO1.DO234;
nRobotIdx.14:= Robot1._UO1.DO235;
nRobotIdx.15:= Robot1._UO1.DO236;
 
nRobotIdx_int:= UDINT_TO_INT(nRobotIdx);
IF nRobotIdx_int >= 1 AND nRobotIdx_int <= GVL.nMaxPoints THEN
    frobot := GVL.aPathData[nRobotIdx_int].fRobot_Pos;
ELSE
    frobot := 0.0;
END_IF
 

Reply
1 Reply
Posts: 2
 lvs
(@lvs)
New Member
Joined: 2 years ago

Hi dxt123,

Just to be sure, do you see the same behavior with Move Relative and Move Velocity?

Can you run an oscilloscope trace directly in the drive to verify whether the same behavior occurs there? It could be a drive setup issue.

Br lvs


Reply
Share: