PLC wont go to Run Mode after I activate my configuration with NC motion task.

2 Posts
2 Users
0 Reactions
153 Views
Posts: 1
Topic starter
(@fink123)
New Member
Joined: 2 months ago

Hi,

I'm working on my uni project. I want to connect my CX8190 PLC to Leadshine Stepper drives DM3E-870 using EtherCat to control some stepper motors. Before I got any hardware I tested everything on my PC (I set up some virtual axes) and was running without any problems. After I got my PLC and drives, when I try to activate any configuration which include NC Task PLC just stays in Config mode (it wont go to run mode). 
 

Reply
1 Reply
Posts: 16
(@duncan)
Eminent Member
Joined: 2 years ago

Late in on this, so I assume you have found an answer, but I would definitely check the licences.
Select SYSTEM > License in the Solution Explorer tree. 

NC axes need TF5000 'TC3 NC PTP' licence.

And the lack of a licence usually leaves you sstuck in config mode.