OPC UA Client can read but not write

3 Posts
2 Users
0 Reactions
470 Views
Posts: 2
Topic starter
(@ob31)
New Member
Joined: 2 years ago

Hello. I have started Siemens SIMIT as OPC Server. Am running 2 clients, UAExpert and TW3. The thing is that i am only able to read the signals, not write to them (have tried turning the other client off). But the same signal can be written to by UAExpert.

Funny thing is also that when twincat asks about linking a variable, it suggests an input even though it is an output.

Any idea?

Cheers

opc2
opc4
opc3
opc1

 

Reply
2 Replies
Posts: 2
Topic starter
(@ob31)
New Member
Joined: 2 years ago

After some searching i realized i had to write to 1 "execute" and "write enable" under controls.

Reply
Posts: 1
(@golizheh)
New Member
Joined: 5 months ago

@ob31 Hi, I have same problem, Can you see where exactly write 1 and write enable?

Reply