Join us today!

Notifications
Clear all

[Solved] EL6090 Newbie question about buttons

18 Posts
3 Users
2 Reactions
889 Views
Posts: 12
Topic starter
(@mirek-boniewicz)
Active Member
Joined: 2 years ago

* I switched to Config

* I switched to Freerun mode

Next I Pressed "Up" in "DIS Inputs", changed tab to Online, and Value is always 0

But I found something that works. In Tree on the left I Clicked Term 6 (EL6090) and in "CoE - Online tab" I selected auto-update.

Then in address 6000 I saw changing of the pressed key from FALSE do TRUE.

EL6090 PLC Something has changed

 

Reply
1 Reply
TwinControls
Admin
(@beckhoffsupport)
Joined: 2 years ago

Member
Posts: 71

@mirek-boniewicz Good catch! To see the most up-to-date CoE parameter values, 'Auto-update' should be selected.

Reply
kolyur
Posts: 12
(@kolyur)
Active Member
Joined: 2 years ago

I'm a bit unclear on your actual problem. In your screenshot you have this line:

bButtonState := BUTTONS.bBUTTON_ENTER;

But in the I/O list you are only showing one linked variable which is the "Up" button, not "Enter."

When the variables are linked properly, are you unable to see them update in your program?

 

Reply
Posts: 12
Topic starter
(@mirek-boniewicz)
Active Member
Joined: 2 years ago

During tests I tried everything and that button's name was changed few times.

Linked variable doesn't changes its state when program is running.

 

Reply
4 Replies
TwinControls
Admin
(@beckhoffsupport)
Joined: 2 years ago

Member
Posts: 71

@mirek-boniewicz Would it be possible for you to share your project? We can look at it and see what's happening.

Reply
(@mirek-boniewicz)
Joined: 2 years ago

Active Member
Posts: 12

@beckhoffsupport Of course I can, but it is a simple one line and few variables

Reply
TwinControls
Admin
(@beckhoffsupport)
Joined: 2 years ago

Member
Posts: 71

@mirek-boniewicz

Can you try this program and check the button states in the Main program when you press the buttons?

 

Reply
(@mirek-boniewicz)
Joined: 2 years ago

Active Member
Posts: 12

@beckhoffsupport Thank you for fast response, but nothing has changed. All buttons' variables  are in FALSE state. I attached screenshot below.

EL6090 PLC After Launch

I will check it twice and back to this after weekend. Thank you very much for help. Best regards.

Reply
Posts: 12
Topic starter
(@mirek-boniewicz)
Active Member
Joined: 2 years ago

@beckhoffsupport Dear Support. I solved problem. I disconnected some modules from rail et Voila! everything is OK.

I left only IO Pins and Display and my old program works fine.

Later I will check power source, connectors and other potentially hardware failures. But now I'm back on track, so I can write again 🙂

Thanks a lot everybody! Have a nice Programmers Day 🙂

Reply
1 Reply
TwinControls
Admin
(@beckhoffsupport)
Joined: 2 years ago

Member
Posts: 71

@mirek-boniewicz Glad you made it work! You can also check EtherCAT topology online to see which modules are causing the issue next time. Have a great Programmer's Day!

Reply
Page 2 / 2
Share: