Converting REAL to 2 WORDS
Some of the Modbus configurations only accept WORD type variables. If you need to convert a REAL value to 2 WORDS, you can use UNION data type to achieve this easily. Different data types in the UNION share the same memory space.
Create a DUT called ST_REAL_TO_aWORD:
TYPE ST_REAL_TO_aWORD: UNION fREAL : REAL; aWord : ARRAY[1..2] OF WORD; END_UNION END_TYPE
Declare the variables in your program:
fRealValue : REAL := 0.81; stData : ST_REAL_TO_aWORD;
You will see that the REAL value is converted to 2 WORDS automatically in the UNION type.
You can also apply this method to other data conversions (BYTE to REAL, INT to BITS, WORD to BYTE etc...) as well.