Join us today!
[Solved] Tag values are not updating in the HMI after a PLC program change
If the values of the tags that you mapped for your TwinCAT HMI program is not updating anymore after a PLC program change, it is most likely naming or the path has changed for those variables.
Go to TwinCAT HMI, then Windows and select TwinCAT HMI Configuration.
Double click the 'Mapped Symbols' on the left menu, select the tags that are not updating or you can select them all, right click and select 'Refresh Mapping'. This will update the mappings for the symbols. Build your application and publish to HMI Server again.
In case you want to say thank you !)
We'd be very grateful if you could share this community with your colleagues and friends. You can also buy us a coffee to keep us fueled 😊 This is the best way to say thank you to this project and support your community.
twinControls - https://twincontrols.com/
- 17 Forums
- 267 Topics
- 942 Posts
- 1 Online
- 722 Members