Join us today!

Resetting Modulo Er...
 
Notifications
Clear all

[Solved] Resetting Modulo Errors - F350 and F351 - Modulo Calculation: Initialization data invalid

1 Posts
1 Users
0 Reactions
481 Views
twinControls
Posts: 114
Admin
Topic starter
(@twincontrols)
Member
Joined: 2 years ago

You may get F350 or F351 modulo errors when you are activating the modulo configuration on the drive. 

modulo error

To reset this error, double click on the drive, in the open window, select 'Clear Error' phase. 

clear error

 

Go to Drive Manager (2) and select 'Modulo Value' (3) on the left menu under Configuration->Scaling and NC parameters. 

Select 'Yes' to schedule modulo init data saving (PreOp -> SafeOp). (4)

resetmoduloerror

 

Activate the EtherCAT OP status on the drive. 

opmode

 

Save the changes and activate the configuration. 

activate configuration

 

 

Reply
Share: