[Solved] Resetting Modulo Errors - F350 and F351 - Modulo Calculation: Initialization data invalid
You may get F350 or F351 modulo errors when you are activating the modulo configuration on the drive.
To reset this error, double click on the drive, in the open window, select 'Clear Error' phase.
Go to Drive Manager (2) and select 'Modulo Value' (3) on the left menu under Configuration->Scaling and NC parameters.
Select 'Yes' to schedule modulo init data saving (PreOp -> SafeOp). (4)
Activate the EtherCAT OP status on the drive.
Save the changes and activate the configuration.