TwinSafe Project - Alias devices issue [can't detect device from I/O tree]
Hi guys.
Having some issues with the safety project.
To sum:
1. New TwinCat project;
2. new Safety project;
3. Scan I/O devices;
4. Target System -> physical device selected (EL 1918);
5. Right click on Alias Devices -> Import from I/O configuration -> and nothing to select 🙄 🙄 ...??
Anyone have experienced this kind of situation?
Can you make sure the device exists in the Slot section?
No device :
Enable Slot:
Now the device appears in the IO Tree list:
In case you want to say thank you !)
We'd be very grateful if you could share this community with your colleagues and friends. You can also buy us a coffee to keep us fueled 😊 This is the best way to say thank you to this project and support your community.
twinControls - https://twincontrols.com/
I can see the device with your tip, but the moment i go to target system and select the EL1918 i can't see it on the I/O tree no more and some configurations change. I don't understand why....
Severity Code Description Project File Line Suppression State
Error For the selected Target System is required a corresponding Alias Device with linking mode "Local".
Anyone knows the meaning of this error?
Hey there. I need to do some updates in here since there were evolution on this.
But for now I want to know if anyone has the idea what this error means?
This error appears when I try to open a PLC project or even from PLC target itself. Already tried to re-install TwinCat but no success