Join us today!
Notifications
Clear all
OPC UA multiple GVLs
Topic starter
Oct 05, 2023 10:57 am
(@finecut)
New Member
Joined: 1 year ago
Hi,
I stumbled across a problem, I don't understand.
If I have my project with just one GVL, just like in all the tutorials etc. everything works just fine, my variables are addressed by GVLname.variablename in the TMC file and UAExpert.
If I add a second GVL however, it will not add another folder that will show up in UAExpert and the variables in the .tmc file will be named .variablename instead of GVL2name.variablename so they all end up in the main folder of the PLC Data Access.
Any ideas?
Reply
1 Reply
Topic starter
Oct 05, 2023 12:06 pm
(@finecut)
New Member
Joined: 1 year ago
I found it, we had a
{attribute 'Tc2GvlVarNames'}
at the top, to use some constants from another GVL.
It didn't like that, obviously.
Removed the attribute and the constants, now it is working.
Reply
Forum Information
- 17 Forums
- 267 Topics
- 924 Posts
- 0 Online
- 737 Members
Our newest member: KarenTox
Latest Post: Watchdog Timers Expiring During Multi Download
Forum Icons:
Forum contains no unread posts
Forum contains unread posts
Topic Icons:
Not Replied
Replied
Active
Hot
Sticky
Unapproved
Solved
Private
Closed